Sprinkler plans show the protection criteria for the pump room with a diesel engine–driven pump based on Ordinary Hazard Group 2. Is this protection criteria acceptable?
ANSWER: No. The fire pump room that houses a diesel engine–driven fire pump will also include a dieselfuel supply. Since the presence of this fuel is considered storage of a combustible liquid, the protection criteria is required to be Extra Hazard Group 2
11.3.3 The entire pump room shall be protected with fire sprinklers in accordance with NFPA 13, Standard for the Installation of Sprinkler Systems, as an Extra Hazard Group 2 space.