Background: I am involved with an existing data center project with following equip:
(1) 12.47kv / 277/480 delta wye utility transformer connected to 3ph/4w, 3,000A service switchboards "1" and "2"(swbd 2 currently fed from swbd 1 via breaker)
Currently two generators (only one on-line at a time) connect to swbd 1 via 3 pole util and gen breakers with transfer controls at swbd. Generator neutral solidly connected to swbd 1.
(2) Due to capacity, an additional utility service transformer will be added to swichboard "2" and tie to "1" removed. Swbd 2 is set up with util and gen breakers and transfer control similar to swbd 1.
(3) Customer wants to parallel the (2) 2MW generators and connect through parallel swgr to each swbd.
(4) Problem: Adding generators with solidly connected neutral will create code violation, interconnecting grounded neutral of two systems, illegal n-g bond.
Adding 4 pole transfer switches is not practical due to costs and space limitation.
(5) Potential solution: Since most of Swbd "1" and "2" loads are 3 phase, provide separate transformer for the 1 phase load (mostly lighting) and change Swbd "1" and "2" and paralleled generators to 3ph/3wire.
Q1) Exist swbds are listed as 3ph/4wire, does anyone have experience with a smilar change, I presume it would be required to have affected swbds field certified as 3ph/3 wire by UL.
Q2) Further, would it be possible to leave swbd #1 and #2 grounded neutral connection as is, remove all neutral load conductors, and connect to 3ph/3w generators. Under this scenario, swbd 1 and 2 would still be listed as 3ph/4w. Since there is no neutral load, generator parallel swbd could be 3 wire. Is anyone aware if this is a code violation? What are implications of ground fault sensing with 4wire but no neutral load.