Part I continued
Generator Rotor Ground Faults
I note that I titled the initial post Generator Ground Faults and of course it should have been Generator Rotor Ground Faults since nothing in the material referred to any other winding except the rotor.
When practical, it is standard practice to install a 64 relay on the machine to monitor the condition of the rotor circuit to ensure that no indavertent grounds are present. When the machine is equipped with collector rings, the installation of a field ground relay is strait forward and for static excitation systems, this relay can be included as a part of the excitation package. This is not the case when the generator is equipped with a Brushless excitation system. Some manufacturers do offer a ground detection system for these installations, but I have found that each manufacturer applies this detection in a different manner and some will not consider offering this feature.
I suggest that if the machine is large or important, you should consider the installation of a vibration monitoring system which will alarm/trip the machine at high levels of vibration. Specific limits and set points should always be provided by the machine manufacturer.
Rotor Ground Faults-Part II
How Do You Find The Ground?
It is necessary to isolate the field winding from the excitation source. Make an insulation resistance test from the rotor winding to the rotor steel. A zero or low reading is conformation that a ground exists. The exact location of the ground is difficult to predict, but on round rotor designs I have always found the problem to be under the retaining ring. This is the portion of the winding which is cannot be restrained by factory installed rotor wedges, the portion of the winding that can flex the most, and in general the portion of the winding that is most susceptible to damage from the rotational forces of operation.
A word of warning,if you have to send the rotor out for a rewind you had better order the new windings in advance. After you have confirmed that a rotor gound exists, you had better get a purchase order for a new winding and then go back on line with a ground fault until the materials are at hand to effect a rewind. Better count on 7-10 days for this effort and do a lot of planning with the repair and rigging experts to get the unit in and out in a safe manner. Removal of a round rotor unit should always be supervised by an individual completely familiar with your specific unit. When the unit is out of the generator, close up the unit with appropriate material to keep contaminants out and install some type of heat to maintain the stator winding above ambient temperature.
Annual Test On The Rotor Winding
One of the conditions I worry about in the rotor winding are turn-turn shorts which do not involve the ground circuit. It is known that round rotor field windings are susceptible to failure in the turn to turn insulation system. In general turn-turn failures are associated withthe initial construction and are corrected before the unit is shipped. Most manufactures conduct a series of tests after each coil assembly is pressed into the rotor steel. These test consists of insulation resistance tests as the rotor progresses through the manufacturing process so that shorted turns can be corrected as early as possible and with the least amount of schedule and cost impact.
One of the test is the A-C Impedance test on the rotor coil assemblies. The machine I mentioned earlier which had 500 turns in the rotor winding and these turns were combined into 6 coil groups per pole. The reason an A-C test is used is that shorted turn DC effects are magnified approximatley ten fold by A-C measurements. Aproximately 6-7 sets( depends on the number of coil assemblies) of A-C Impedance tests are conducted as the machine goes manufacturing. The final test is conducted after the machine is at rated speed and after final balance. This impedance is corrected to a nominal value and is available to the customer-all you have to do is ask for the information. A test at standstill is also made and this is the test data you need. You need the voltage at which the test was made and the A-C current which results from this test. The standstill factory test is the benchmark you will use in the field to confirm that you have or do not have turn-turn shorts.
In the field it is necessary to disconnect the excitation system and have a variable A-C voltage source and install a 5-10 amp meter in series with the source. For the machine I mentioned above the A-C test voltage was 100 volts and the expected current was 1.3 amps when the rotor was at ambient temperature ( 25 deg. C). A 5 watt variac should be sufficient. Corrections have to be made for the ambient temperature. The Z value for this machine was 76.9 ohms.
If the field test results differ by more than 10 % from the factory tests, you have a reason to be concerned. It is time to call in and or consult with the factory experts.
I should add that the remedy for a turn-turn short is the same as fixing a rotor ground-it's a big problem and it's time to get out the checkbook.
You should not extrapolate the 100 volt rotor impedance test to all manufacturers-this test just applies to GE machines. I know that Brush (Great Britian) recommmended 36 volts and 4.2 amps and a Z= 8.6 ohms for a unit that was rated 57 MVA, 13.2 KV and 3600 RPM.
I hope this answers your questions concerning rotor earth faults.