Dear eskim,
My sporadic thoughts-
a) Do you lose all the DEGs in every incident or just one black sheep or at random - lowest loaded?!
b) Are DEG and STG synchronized on the same bus with similar step up/direct arrangement?
c) Why operator cannot go to outsite? If you trip DEG breaker alone will you be closing it back from remote? What if closing is delayed - remember - long duration no load running can also be bad for the Engine.
Your first question:
There is nothing called as Generator stopping! If breaker fails to open when fuel is cut off to the engine and the excitation breaker has opened then the DG set enters Motoring mode. If local grid is sufficiently strong, then the DG set will MOTOR by consuming about 5 - 25 % of the rated active power (called motoring power - find the figure for your set) and nearly 100~300% reactive power. If excitation is still on then the reactive power can still be forward! but the set MOTORS. This may not go on for long since the piston rings will jam due to non-lubrication and subsequent overheat(remember, the fuel oil/carbon partially lubricate!) following which an explosion of unburnt fuel might take place, gearbox (if provided)/shaft might suffer due to 'increased torque', etc. Books and experts recommend a reverse power setting of 50% of the Motoring power (= 5 to 25% of rated power).
A LBB scheme, if active and thoughtfully applied, might disconnect that section of the bus and save the DEG set.
Second part: If the power excursions are of transient nature you might run the risk of overspeeding the Diesel Engine. So cut of fuel to the engine as well as trip the GCB if motoring is confirmed. The time delay for confirmation could be set with some operational experience 0.5 to 1 sec or even more. Take the advice from the set Vendor. Put an alarm contact from poer relay before timer to see how often are the power excursions?
Part 3: Think of adjusting the governors of both the DEGs and STGs to different droop settings so that the change of load does not impose more change on the DEG sets and least on STG. Change load bus if that is possible at all, sometimes very close to miracles do happen that can be explained later.
Best regards,