electrouw
Electrical
- Jun 6, 2010
- 16
Good day.
We are in the process of commissioning a 625kVA (at 0.8 PF) natural gas reciprocating synchronous genset. The genset is connected on the LV side of a 1500kVA step up/down transformer.(11kV > 415V). For the most part our plant will be consuming the electricity but at some stages we will be exporting to the grid.
We have been able to take the genset up to 400kW on a resistive load bank with no problems.
Recently we were able to successfully sync to the grid. For some mysterious reason as soon as we are connected to the grid the current in all three phases start jumping. I'm talking from 50A to 700A back to 50A within a second. As a result of this the power factor oscillates between -0.2 and 0.2 centred around 0.95.
The voltage on all three phases is fine at 250V.
It might also be worth mentioning that the neutral current are pretty consistent at 20A. Another thing that might be a reason or a result, is the THD mostly made up of the 3rd order harmonic.
THD of grid alone = 2.5% ( mostly due to 5th order harmonic, induction motors in the plant)
THD of generator on loadbank = 2.5% ( mostly due to 3rd order harmonic)
THD of system ( generator connected to grid ) = 6%
( once again mostly due to 3rd order harmonic)
It would be much appreciated if anyone can shine light on this strange phenomina. Together with the Genset's own protection, I have a Deif GPU-3 overlooking the protection. This unit is not a sync-check device but it does show that the phase angle between the grid and the generator is 0 while synchronised.
I might also add that the throttle actuator is acting very different when connected to the grid as opposed to the load bank. When connected to the grid it constantly jerks between about 20 and 70 degrees ( range is 0 to 90 degrees 90 being fully openned). Could this induce the big variation in current.
As far as I am concerned the system is meant to switch from speed/frequency control to power factor control as soon as we are synched - this could infact not be the case.
I've attached a pdf with the current data, and I can add the voltage and power information if need be.
Thanks is advance!
We are in the process of commissioning a 625kVA (at 0.8 PF) natural gas reciprocating synchronous genset. The genset is connected on the LV side of a 1500kVA step up/down transformer.(11kV > 415V). For the most part our plant will be consuming the electricity but at some stages we will be exporting to the grid.
We have been able to take the genset up to 400kW on a resistive load bank with no problems.
Recently we were able to successfully sync to the grid. For some mysterious reason as soon as we are connected to the grid the current in all three phases start jumping. I'm talking from 50A to 700A back to 50A within a second. As a result of this the power factor oscillates between -0.2 and 0.2 centred around 0.95.
The voltage on all three phases is fine at 250V.
It might also be worth mentioning that the neutral current are pretty consistent at 20A. Another thing that might be a reason or a result, is the THD mostly made up of the 3rd order harmonic.
THD of grid alone = 2.5% ( mostly due to 5th order harmonic, induction motors in the plant)
THD of generator on loadbank = 2.5% ( mostly due to 3rd order harmonic)
THD of system ( generator connected to grid ) = 6%
( once again mostly due to 3rd order harmonic)
It would be much appreciated if anyone can shine light on this strange phenomina. Together with the Genset's own protection, I have a Deif GPU-3 overlooking the protection. This unit is not a sync-check device but it does show that the phase angle between the grid and the generator is 0 while synchronised.
I might also add that the throttle actuator is acting very different when connected to the grid as opposed to the load bank. When connected to the grid it constantly jerks between about 20 and 70 degrees ( range is 0 to 90 degrees 90 being fully openned). Could this induce the big variation in current.
As far as I am concerned the system is meant to switch from speed/frequency control to power factor control as soon as we are synched - this could infact not be the case.
I've attached a pdf with the current data, and I can add the voltage and power information if need be.
Thanks is advance!