Generator Neutral Grounding Resistance Sizing 3

Status
Not open for further replies.

mahmoudmaged

Electrical
Nov 4, 2009
4
I have a generator 3000 kVA, 400 V, 50 Hz that requires a neutral grounding resistance for short circuit protection.

How can i size that resistor in detailed steps?
 
Replies continue below

Recommended for you

Step one: Divide the phase to neutral voltage by the desired maximum ground fault amps. This gives you the resistance.
Step two: Multiply the voltage by the desired maximum ground fault amps. This will give you the watts that will be dissipated by the resistor under worst case conditions.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
I think Bill got it said. Now all you need to do is select an appropriate CT and Relay to make it work for you.

Alan
 
There's a few IEEE standards for neutral grounding sizing for synchronous machines. Usually shows up when you search for IEEE standards with the keyword "synchronous".
 