Generator netral grounding transformers

Status
Not open for further replies.

ters

Electrical
Joined
Nov 24, 2004
Messages
247
Location
CA
I'm working on a generation upgrade project where the client wants to replace existing oil filled generator neutral grounding transformers. They are 14 kV/240V 10 kVA (with a load resisitor of 1 OHM). Is there any reason why only oil type of the transformer should be employed for this purpose or an epoxy dry type would be as good assuming it enclosure can fit in a rather limited space. Thank you for any info.
 
A dry-type should be OK. Just make sure the primary has a good BIL.
 
All the ones I have seen on hydro generators are dry type
 
 
Legacy stator-grounding literature like IEEE C37.101 refers to the process as “distribution-transformer grounding,” and to some degree fluid-insulated habits probably die hard. For smaller transformers, flammability safety and high BILs available in epoxy-insulated drytypes, I can’t much reason not to use them.
 