Is it in the generator or the drive? Hydrogen cooled or air cooled.
Assuming that the vibration is in the generator not the turbine:
The main question is what is the vibration frequency?
If it subsynchronous, it could be misalignment between the turbine and generator unloading the generator inboard bearing.
If it is 1X and in the generator, it could be a rub, but rubs are pretty unusual in generators. Does it happen when you flash the fiel? Could be a hot spot in the exciter. I saw one once that would go to 10 mils pp immediatly on flashing the field, even before any load was applied.