Hi Volkan.
In your case you have several options.
You need check also cost of each solution.
We start from best technical solution.
1. Two zigzag transformer each one on separte bus.
zigzag transformer will be earted (grounded) via high speed earht switch. ( with grounding resistor or without, is depends on earht fault calculation).
what is a benefit of this solution.
very flexible system with logic of coupler position, all time in all configuration you can choice only one virtual earht point. Good option for ET maintanance.
But you need two aditional feeders ( CB, CT, control and protection )for these earth trafo's.
Possible also connect them to bus via disconectors, in this case some short circuits or bucholz on ET open all infeeds on this bus.
2. Four earhing points , HRG connect to generators via high speed grounding switch, two ET you connect to main trafo (between trafo and CB), grounding of ET neutral point via high speed grounding switch (with resistor or without).
You add logic for choice only one virtual earth point.
More equipment, ET in differential protection zone.
3. Same to point 2 , but without any high speed grounding switch and without logic.
It's also work without any problem, we have more or lees same system on one industrial power plant (but without coupler)more from 20 years. E/f current flow between 4 points ( actually is not big problem, all TR and GEN in the same place). Protection system against E/F it's 51N (you put toroid CT on each grounding point).But I think possible discuss about protection after your choice of grounding method.
I'm sure you recieve many other recommendations.
Best Regards.
Slava