I was just given one of those "standard details" for a generator foundation to be blessed. Nobody knows where it came from, but it has been used on this MEP's drawings since the dawn of time.
To support a 2000 lb generator, the detail has an 18" slab with rebar at 12" on center top and bottom in the long direction and 6" on center top and bottom in the short dimension. The edges of the slab extend to 4' deep with hairpin-type bars. The entire structure is monolithic.
The rebar size is not specified and the slab is not dimensioned, except for the depths. This is completely generic, so there is no site information to consider.
- The slab is exposed to freezing temperatures - wouldn't frost heave the slab anyway because it is only 18" below grade? Shouldn't there be some sort of compressible insulating material under the slab portion to isolate it from frost heave.
- Is it necessary to drop the sides to 4'? Couldn't a lightly loaded slab like this be permitted to "float", provided all of the connections were flexible?
Miscmetals
To support a 2000 lb generator, the detail has an 18" slab with rebar at 12" on center top and bottom in the long direction and 6" on center top and bottom in the short dimension. The edges of the slab extend to 4' deep with hairpin-type bars. The entire structure is monolithic.
The rebar size is not specified and the slab is not dimensioned, except for the depths. This is completely generic, so there is no site information to consider.
- The slab is exposed to freezing temperatures - wouldn't frost heave the slab anyway because it is only 18" below grade? Shouldn't there be some sort of compressible insulating material under the slab portion to isolate it from frost heave.
- Is it necessary to drop the sides to 4'? Couldn't a lightly loaded slab like this be permitted to "float", provided all of the connections were flexible?
Miscmetals