keewee -
Before I go any further, I just have to remind readers that I am approaching this subject from a UK regulatory / statutory perspective.
In the UK it is illegal to operate any electrical distribution network (of any size) without it being efficiently earthed.
A standby generator installation requires to have, amongst other things, a measured independent earth electrode so that should the utility supply network 'disappear' (eg overhead networks flattened by storm-force winds), the standby genset can still supply the electrical installation AND be referenced to the general mass of earth.
Now, if the utility supply is of the separate neutral/earth variety (neutral only earthed at ONE point, back at the local substation - that's TN-S to non-utility people), then you are quite correct; the neutral is required to be switched too using 4-pole switchgear.
If, however, the supply is from a network where the neutral and earth conductors are combined, as in protective multiple earthing (PME, or TN-C-S, if you prefer), then the genset changeover switchgear is only required to be 3-pole. 4-pole is acceptable, but it is not a requirement. The neutral/earth conductor from the utility is efficiently earthed at least at one point (the substation) and most probably at many other points too, just like your multiply earthed neutral network.
Now, regardless of which flavour of utility supply you have, if the utility provides you with an main supply earth terminal, you are required to bond it solidly to your independent earth electrode, and hence to the generator starpoint. In the UK some LV supplies such as petrol filling stations are not afforded an earth terminal.
If you have a PME or MEN supply, the neutral of the utility supply is also directly bonded to the generator neutral as a consequence of the network earthing arrangement - so only 3-pole switching is required. If you elect to utilise a 4-pole switch, the generator neutral/earth is bonded via the main earth terminal to the utility neutral/earth anyway, so why bother?
I accept what you say about unbalanced loading of the genset 'imposing' a rise of potential in the overall earthing but as everything is bonded together and the prospective potential gradients are small, there are no significant step, touch or transfer potential issues.
Any utility work on the neutral conductor, cable sheath or substation earth electrodes already takes into account the risk of transfer potential due to unbalanced generators, poorly wired (reverse polarity) installations and genuine earth faults as part of published live working procedures.
FYI, the statutory basis for electrical installations in the UK is the Electricity Safety, Quality and Continuity Regulations 2002, which may be viewed at-
The industry standard for interfacing utility supplies to generator installations is Engineering Recommendation G59/1, published by the technical documentation wing of EA Technology (
However, the document I think you are seeking is the sister document to G59/1, which rejoices in the equally forgettable title of Engineering Technical Report 113 (or simply ETR113). It is published by the same body and contains the technical treatment with diagrams that you seek. It is VERY pricey though, coming in at over 200 UKP per copy.
Finally, in the UK, fixed electrical installations at LV are regulated by the current edition of the IEE Regulations for Electrical Installations, commonly known as the Wiring Regs and less commonly known as British Standard 7671. Specific issues related to generators are addressed in this document too.
As I said in my first reply, your initial point of reference should be the operations engineering department of your supply utility. An engineer from that department would/should be able to give you all the information you need.
regards