Rajt,
I see where you are coming from, my apologies, I didnt explain fully. Take a typical say 20Kva 400/230v gen set. It has 3xphase, 1xneutral and a separate dedicate earth conductor, (no earth fault relay). The current generated due to any fault to earth will be carried by that dedicated earth conductor. In this case the required connection of the neutral point of the set to earth then has little to do with limiting fault current for the purposes of discrimination as you desribe (I take it that you were assuming no separate dedicated earth conductor when you made your response).The purpose of the connection of the star point to earth is to establish a reference and ensure that the neutral conductor remains at or about earth potential. I was just wondering why 10 ohms was set as an upper limit. Regards,
Lyledunn