Hello everyone,
Great website, great knowledgeable people here resolving key issues found on sites.
I work for an Independant Commissioning Agency which is responsible for the verification of all mechanical/electrical systems within buildings.
I work up here in Southern Ontario, Canada.
I am working on a new construction hospital project.
The project has:
qty:2 CAT gensets 3516 Engine, 825 Alternator Frame, 2000kW, 2500kVA rating at 0.8pf. its is a three phase system with a line voltage of 4160V. Excitation is PM.
There is an operating standards Hospital code in Canada where Emergency Life System power has to be restored via the generators within 10 seconds of a loss of utility power.
The two generators are meant to parallel and synch together to share the load however to meet the above code, the generators race to the emerg. bus and the first one there will pick up the Emergency Life Safety Load.
An issue has come up, we have an advanced load shedding system designed and implemented in this project, however all of the power control for tripping the load shedding breeakers are not on UPS and/or DC battery power.
Therefore the Generators have to come online and assume all of this load before it can shed via its controls.
There is an estimated design of up to 3MW of power on the Emergency Bus. Which means that since these loads cannot be dropped until the Generators come online the first Genrator that comes onto the sytem will see a 3MW block load hit.
With your various experiences, what is your expectation of one generator taking a 150% block load hit. Each generator is rated a 2MW. Will the field voltage in the voltage regulator break down thereby losing the generator and essentially all source of emergency power.
Much thanks for your help.
Great website, great knowledgeable people here resolving key issues found on sites.
I work for an Independant Commissioning Agency which is responsible for the verification of all mechanical/electrical systems within buildings.
I work up here in Southern Ontario, Canada.
I am working on a new construction hospital project.
The project has:
qty:2 CAT gensets 3516 Engine, 825 Alternator Frame, 2000kW, 2500kVA rating at 0.8pf. its is a three phase system with a line voltage of 4160V. Excitation is PM.
There is an operating standards Hospital code in Canada where Emergency Life System power has to be restored via the generators within 10 seconds of a loss of utility power.
The two generators are meant to parallel and synch together to share the load however to meet the above code, the generators race to the emerg. bus and the first one there will pick up the Emergency Life Safety Load.
An issue has come up, we have an advanced load shedding system designed and implemented in this project, however all of the power control for tripping the load shedding breeakers are not on UPS and/or DC battery power.
Therefore the Generators have to come online and assume all of this load before it can shed via its controls.
There is an estimated design of up to 3MW of power on the Emergency Bus. Which means that since these loads cannot be dropped until the Generators come online the first Genrator that comes onto the sytem will see a 3MW block load hit.
With your various experiences, what is your expectation of one generator taking a 150% block load hit. Each generator is rated a 2MW. Will the field voltage in the voltage regulator break down thereby losing the generator and essentially all source of emergency power.
Much thanks for your help.