ThePunisher
Electrical
- Nov 7, 2009
- 384
We have a 5.5MVA, 4160V generator connected to a bus with some static loads and a couple or 4kV motors. On an island mode scenario, if we start the largest motor in place, the load flow shows a surprisingly 42% voltage drop on the 4160V MCC bus. The generator terminal voltage set on the study is 1.036P.U. nominal voltage. The load flow calculation does not dynamically calculate exciter/AVR response, but considering even a 1.10 P.U.terminal voltage will not help.
The generator datasheet indicates maximum allowed starting load of 10.2MVA at 10% P.F. with maximum voltage drop of 15%, voltage drop at sudden increase of rated load = 7% and voltage rise at sudden drop of rated load =9%
I would appreciate some experience and expertise on what the above generator specs means?
The generator datasheet indicates maximum allowed starting load of 10.2MVA at 10% P.F. with maximum voltage drop of 15%, voltage drop at sudden increase of rated load = 7% and voltage rise at sudden drop of rated load =9%
I would appreciate some experience and expertise on what the above generator specs means?