jmbelectrical
- Jul 16, 2011
- 126
I will be performing an inspection at a residential property next week. The electrical service is 240/120-volt, single-phase, three-wire, 60Hz. It is equipped with a 60kW, whole-house, standby generator and a 13kW PV system. The PV system connects to a loadcenter/panel via a grid-tie inverter. The loadcenter/panel is on the load side of an automatic transfer switch. The system is arranged such that the generator and PV system can operate in parallel. No interlocks have been installed between the generator and the inverter. The PV system is approximately six years old and the generator is approximately three years old.
The PV system is no longer producing power. (I do not know if the fault lies with the inverter, the PV panels, or some other component.) The property owner has alleged that the generator installation - specifically, that the generator can be paralleled with the PV system - resulted in damage to the inverter. I am aware of the dangers of paralleling generators and PV systems, however, it is my understanding that the damage typically occurs at the generator as a result of the PV system backfeeding it. In this case, with the generator size being nearly five times that of the PV system, could the generator have backfed the inverter? What other failure mechanisms could this be attributed to?
Any input would be greatly appreciated.