PaulUK,
You can have two or more generators running in a sort of isochronous mode, but to do this you need to have an overall controller for each generator "above" the governor. With Woodward equipment, that would mean using an EGCP2 for each generator. One EGCP2 ends up being a master unit and trims all the other generators via their EGCP2 controllers. The trimming is done via serial link between all of the EGCP2's. This system only works when the generators are running in parallel with each other but isolated from the grid. EGCP2's are fairly expensive.
If you did not have such a system, I think it would not really be possible to operate two or more generators in isochronous mode. To do so they would need to be identical machines, have identical responses and all the governors would need to have identical control settings. Not practically achievable I think.