Back in the day, I started up GE's first European Bypass design turbine outside of Europe (Itabo II in the Dom. Rep.)
It had a Sulzer 100% Bypass system composed of HP and LP bypass valves and 100% flow capacity compact coolers for both main and reheat steam. The unit could take a full load rejection and the when the unit rpm returned to synchronous the Intercept on one side would begin to open to control and maintain synchronous speed...when the generator reconnected the station was in island mode (no external system load) the emergency diesel would stop... all in about 15 minutes as I recall. The Intercept valve was the controlling valve.
Also, when GE closed its Lynn Mass facility, they had let go all the controls test personnel. The last MkIII system to ship (for Talkha, Egypt combined cycle station) was not tested and I was asked to do testing on these last two systems. I was surprised when I got there and saw that the control valve circuit had 3 separate ramp curves and that there was only one control valves for each turbine AND that the control valve was a intercept valve from a cancelled order sitting on the shelf. If it can be done, they'll usually do it before losing money. The Intercept valve size and flow characteristics required the special control ramps to make linear steam flow for the 100mw steam turbine in a combined cycle configuration with sliding pressure control.
ps: Have not seen a reverse flow turbine...have seen reversing stages for marine applications though...???