Hi obewan9043
It is difficult to understand your problem due to lack of some data.
First of all you need a generator. If your turbine is 125 MW you need a 150 MVA generator with 13-14% xd". Also you need an Unit Auxiliary Transformer. If you intend to supply from this transformer the start induction motor ,the excitation and the compressor and if you intend to use for example oil instead of gas probably some 17-20 MVA would be necessary . If you intend to supply from this UAT also the HeatRecoverySteamTurbine you'll need another 5-7 MVA. So ,let say, a 25 MVA 8% will be ok.
If a Generator CB will be provided the GE gas turbine may start using this UAT.
Else you will need a Reserve Auxiliary Transformer connected directly to the Utility 132 KV Grid. In this case the short circuit current will be a little higher.
If the Utility System 132 kV may be provided with a 50 kA CB then the System Short circuit will be 11431.5 MVA .
In the first case [ supply from UAT] the short circuit current I"sc on the Generator terminals may be 132 kA ,on the 6.3 kV bus bar 27.5 kA, on the 600 V bus bar 7.4 kA and on the 380 V about 12.5 kA.
Best Regards