- Apr 5, 2005
- 24
One of our clients had a Trip Coil burn up on one of their GE 69kV Circuit Breakers. They found it after a fault had occured on the breaker's line, causing the breaker failure relay to trip the sub offline.
The odd thing is that the prints for these breakers show them having two trip coils, so the protection logic utilized that fact in a way to make sure both coils were tripped before breaker failure would be initiated.
Well, we looked at the breaker and the "two" trip coils weren't what I expected...they were what appeared to be four leads coming out of the same coil. It didn't appear that the two coils were insulated from each other in any other way besides, perhaps, the conductor's insulation. In any case, either I'm missing something, or that design is less than what it should be.
Anybody seen or worked with these who could offer some insight?
Thanks
The odd thing is that the prints for these breakers show them having two trip coils, so the protection logic utilized that fact in a way to make sure both coils were tripped before breaker failure would be initiated.
Well, we looked at the breaker and the "two" trip coils weren't what I expected...they were what appeared to be four leads coming out of the same coil. It didn't appear that the two coils were insulated from each other in any other way besides, perhaps, the conductor's insulation. In any case, either I'm missing something, or that design is less than what it should be.
Anybody seen or worked with these who could offer some insight?
Thanks