My experience is the same as dpc, it has more to do with the number of operations. VCBs are expected to last in the area of 10k operations at best, but will need mechanical adjustment at intervals of just 500 operations. A Contactor on the other hand is designed to last 200-300k operations with 25k before needing service. If you are cycling the motor once per day, a VCB would need adjustment in under 2years, vs a VC not needing it for 60+ years.
There is also a difference in the vacuum bottles used. Contactor vacuum bottles are designed to reduce “chop current” on opening, which can damage motor windings. The metallurgy of the contact material is optimized to minimize this, but that reduces its ability to handle high interrupt current, hence the need to be paired with fuses. VCB vacuum bottles are usually not designed for reducing chop current because their main function is protective, not control. The metallurgy in the contacts is tailored to handle higher interrupt current, not chop current, resulting in the chop current typically being 5x that of a VC. If you are not cycling a motor on and off very often, that’s not as big of an issue.