nightfox1925
Electrical
- Apr 3, 2006
- 567
We have a 13.8kV solidly grounded system where the short circuit is relatively high.
One of my colleagues are specifying a NEMA E2 class starter to feed a padmounted distribution transformer. The 51G at the secondary is proposed to be wired to to trip the upstream contactor.
My concern is that the contactor is not rated to interrupt the amount of GF current on this solidly grounded 13.8kV, so I am pushing for a VCB instead. His argument is that as long as the fuse is current limiting, the contactor will be able ti interrupt....there is something wrong with that argument. If the GF current is high enough, then the fuse will interrupt a lot faster than the contactor. The concern lies on the gap between the fuse curve and the contactor rated breaking current. Since this is feeding a transformer, the fuse curve will be so chosen that no point on its TCC curve will touch the inrush point, hence, a gap will be there.
Any comments?
One of my colleagues are specifying a NEMA E2 class starter to feed a padmounted distribution transformer. The 51G at the secondary is proposed to be wired to to trip the upstream contactor.
My concern is that the contactor is not rated to interrupt the amount of GF current on this solidly grounded 13.8kV, so I am pushing for a VCB instead. His argument is that as long as the fuse is current limiting, the contactor will be able ti interrupt....there is something wrong with that argument. If the GF current is high enough, then the fuse will interrupt a lot faster than the contactor. The concern lies on the gap between the fuse curve and the contactor rated breaking current. Since this is feeding a transformer, the fuse curve will be so chosen that no point on its TCC curve will touch the inrush point, hence, a gap will be there.
Any comments?