In IEC 60269-2-1 it is presented:
Section I Table VI for "gG" fuses[up to 16 A].
Section V Table VI for "gD" and "gN" fuses [from 10 to 6000 A].
Section VI Table MM for "gU" fuses[from 100 to 630 A].
Since IEC 60269-1 ch.7.7 states:
"The operating I2t values verified according to 8.7 shall be less than, or equal to, the characteristics stated by the manufacturer in accordance with 5.8.2 or specified in subsequent parts.", then I think the value shown in Table 6 as I^2tmax could be less than
manufacturer specified.