I have (1) Class J 600A fuse that blew feeding a group of motors. The load consist of 20 fan motors plus a small heater. All of the motors have individual fusing and IEC style overload protection(several OL's tripped but none of the fuses protecting the individual motors did). When the fuse blew the load was roughly 240amps (12 to 14 motors running). I have checked wires to ground with ohmeter , resistance between all motor leads (4ohms), Operation of all the contactors with the 480volt power off, and terminations at Main Fuse Disconnect. The nameplate for 19 of the motors 27Amps and 1 is 14Amps. Would anyone have a suggestion to what else I should check?