We have two rail cars that run happily on their own generators. This costs money for fuel that is otherwise provided by HEP as part of the hauling deal so it is VERY desirable to use HEP when it's available. If either of these cars are put up against the engines the entire hookup described above works fine but the main HEP contactor trips on "fault". If the car is placed at the back of the train there is usually NO problem.
These cars consist of HEP delivered thru a 480V, 50A breaker to a bus-bar system. A 480V - 240V transformer bank,(3 dry transformers), then feeds all the 3 phase loads and single phase loads like ovens. The 240V is transformed down to 120V to feed single phase loads.
I'm looking for suggestions on why these cars are tripping out the HEP.
################### Ancillary Info ################
H.E.P. = Head End Power
HEP is power provided by a locomotive to Amtrak passenger cars. It is passed down four huge cable sets. The plugs are about 60 pounds apiece.
Each of the cable sets has 6 conductors. One for each phase (Delta) and then three safety wires. To prevent arc-flash casualties the pins are staged. The three safety pins engage last and disengage first.
The power is 480V @ 1,400A split across these four cable sets. Once all the cables are correctly engaged a contact closes in the engine that turns on a light signifying that the main contactor can close. The engineer can then press a button that closes the contactor that energizes all four HEP cables. Any pin disengagement automatically drops the HEP.
The cables run in pairs down both sides of all cars. 72VDC is sent down the three safety wires of one cable and at the end of the train are "looped back" with a full cable jumper returning down the adjacent three safety wires of the neighboring cable. These three signals are ANDed together at the engine to confirm two completely connected HEP circuits on each side of the train.
Keith Cress
Flamin Systems, Inc.-
Keith Cress