Jan 16, 2019 #1 Eric L. Structural Joined Jan 16, 2019 Messages 2 Location US I've been told that NFPA requires hanger rod be threaded down to the pipe in a swivel ring hanger. Anyone know where in the NFPA this requirement is listed?
I've been told that NFPA requires hanger rod be threaded down to the pipe in a swivel ring hanger. Anyone know where in the NFPA this requirement is listed?
Jan 16, 2019 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,776 Location US It's not required. It is an option to prevent uplift as is required for some installations. Look in Chap 9 of NFPA 13 (2016) for further information. Travis Mack, SET, CWBSP, RME-G, CFPS MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote
It's not required. It is an option to prevent uplift as is required for some installations. Look in Chap 9 of NFPA 13 (2016) for further information. Travis Mack, SET, CWBSP, RME-G, CFPS MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Jan 17, 2019 Thread starter #3 Eric L. Structural Joined Jan 16, 2019 Messages 2 Location US Appreciate the reply Travis; I had already went through Chapter 9 a couple times, but didn't see the requirement. Thought I'd confirm on here. Upvote 0 Downvote
Appreciate the reply Travis; I had already went through Chapter 9 a couple times, but didn't see the requirement. Thought I'd confirm on here.