cmelguet
Electrical
- Jul 19, 2009
- 64
Hi, I am involve in a project where we are running several 3 phase circuits of 33 kV using single phase conductors arranged in a trefoil formation. The cables are installed on a FRP cable ladder which is no good as a grounding conductor. The circuits lengths is around 1000 m, and all of the circuits goes from the main substation GIS switchgear to transformers 33/4.16 kV unitsubstations located around the plant.
Question: NEC requires to run a grounding conductor with every circuit. Normally the cable ladder is good enough for this. Since in this case i have an FRP cable ladder what are my alternatives?. Should I run an aditional grounding conductor for each circuit?. I understand the grounding grid is not good enough as a grounding conductor, even if all the grounding grids of the plant are joined together.
Regards,
Cristian
Question: NEC requires to run a grounding conductor with every circuit. Normally the cable ladder is good enough for this. Since in this case i have an FRP cable ladder what are my alternatives?. Should I run an aditional grounding conductor for each circuit?. I understand the grounding grid is not good enough as a grounding conductor, even if all the grounding grids of the plant are joined together.
Regards,
Cristian