Use of VFD output side contacter for E-stop
jOmega said:
"Any contactor that is rated my its manufacturer for ac motor duty, is ok. Suggest NEMA rated as opposed to IEC as an IEC contactor will likely shorten motor life."
ScottyUK asked what the difference was, to which jO replied:
"The IEC contactors have a shorter throw length and studies have shown this to cause motor insulation failures."
afterhrs and GGOSS have requested a additional discussion and it makes sense to start a new thread as afterhrs suggested
Last papers I remember were over 10 years ago ... within a couple of years of the IEC contactors being introduced in USA. Don't recall if article was in trade pub. or in IEEE journal.... Might have a copy somewhere in my archives...
Will look for it. Otherwise I don't have access to the source material.
From what little memory I have left, the gist of the research came about from reports of motor insulation failures when operated with IEC contactors. The investigation led to the fact that the shorter throw length of the IEC contactor promoted more arcing in the process of opening the circuit. This arcing produced voltage stress levels of very high dv/dt that resulted in breakdown of motor insulation.
The NEMA contactors, having a longer throw length, which assures that the arc is extingushed.
Going back to fundamentals where E = L di/dt .... picture the process of opening a set of contacts.....as they begin to separate, arcing occurs.... as the distance between the contacts increases, a point is reached at which the arc is not supported.... and it dies... as a consequence of the distance.... as opposed to the shorter throw length configuration whereby the extinghishing of the arc occurs after some time as a natural diminuation of the decaying energy.
Allen-Bradley is said to have also performed an investigation into this phenomena not long after they introduced their Bul. 19x IEC contactors... and that the investigation substantiated the motor insulation failures and showed the cause to be related to the shorter throw length. That report never saw the light of day and from a marketing aspect, I'm sure you understand why.
That's the recollection....
Now it may be, that IEC contactors have since addressed this issue... and effected product modifications to eliminate this problem.
But not being aware of same, I made the statement about using NEMA instead of IEC contactors.
jOmega
p.s. interesting add to the above comments about Allen-Bradley is this statement in their application note #114 as follows:
"3. Smaller, Iess expensive motors that have less of a design safety factor will be more susceptible to possible damage from any source. (IEC contactors can cause failures in lesser design motors)"
I leave it to you to decide for yourselves what they mean by "lesser design motors"....... non-inverter rated perhaps ?
jO
The app. note can be found at:
Bulletin 1336 Plus Igbt Technology Application Note # 114
Use of VFD output side contacter for E-stop
jOmega said:
"Any contactor that is rated my its manufacturer for ac motor duty, is ok. Suggest NEMA rated as opposed to IEC as an IEC contactor will likely shorten motor life."
ScottyUK asked what the difference was, to which jO replied:
"The IEC contactors have a shorter throw length and studies have shown this to cause motor insulation failures."
afterhrs and GGOSS have requested a additional discussion and it makes sense to start a new thread as afterhrs suggested
Last papers I remember were over 10 years ago ... within a couple of years of the IEC contactors being introduced in USA. Don't recall if article was in trade pub. or in IEEE journal.... Might have a copy somewhere in my archives...
Will look for it. Otherwise I don't have access to the source material.
From what little memory I have left, the gist of the research came about from reports of motor insulation failures when operated with IEC contactors. The investigation led to the fact that the shorter throw length of the IEC contactor promoted more arcing in the process of opening the circuit. This arcing produced voltage stress levels of very high dv/dt that resulted in breakdown of motor insulation.
The NEMA contactors, having a longer throw length, which assures that the arc is extingushed.
Going back to fundamentals where E = L di/dt .... picture the process of opening a set of contacts.....as they begin to separate, arcing occurs.... as the distance between the contacts increases, a point is reached at which the arc is not supported.... and it dies... as a consequence of the distance.... as opposed to the shorter throw length configuration whereby the extinghishing of the arc occurs after some time as a natural diminuation of the decaying energy.
Allen-Bradley is said to have also performed an investigation into this phenomena not long after they introduced their Bul. 19x IEC contactors... and that the investigation substantiated the motor insulation failures and showed the cause to be related to the shorter throw length. That report never saw the light of day and from a marketing aspect, I'm sure you understand why.
That's the recollection....
Now it may be, that IEC contactors have since addressed this issue... and effected product modifications to eliminate this problem.
But not being aware of same, I made the statement about using NEMA instead of IEC contactors.
jOmega
p.s. interesting add to the above comments about Allen-Bradley is this statement in their application note #114 as follows:
"3. Smaller, Iess expensive motors that have less of a design safety factor will be more susceptible to possible damage from any source. (IEC contactors can cause failures in lesser design motors)"
I leave it to you to decide for yourselves what they mean by "lesser design motors"....... non-inverter rated perhaps ?
jO
The app. note can be found at:
Bulletin 1336 Plus Igbt Technology Application Note # 114