joepegas
Mechanical
- Jan 7, 2004
- 8
My company has been having a problem with the freeze stat's tripping and shutting-off the air handlers occasionally under cold conditions. Originally I was led to believe that is was a condensate logging problem becuase Spirax-Sarco proposed replacing the existing F&T traps with trap-pumps. I didn't like this idea and starting digging to find out that the freeze stat's were tripping when the temperature sensor that controls the steam valves was reading 75 degrees or so. There are four coils in a 2X2 config. and four AHU's. Each coil has a freeze stat and the temp sensor runs diagonally across two coils (2 and 3). It was suggested that I use another temp. sensor across the other 2 coils (1 and 4). I also thought about using a sight glass and pressure gauges to check if the coils were backing up. One issue is that the problem happens occasionally on random AHU's and I can't figure out how to trace the problem. Also, there are vacuum breakers on the inlet side and the modulating valves are pneumatic. I would appreciate any help, thanks.