COEngineeer
Structural
- Sep 30, 2006
- 1,186
When I design frame garage floor I usually use 1.5 DL (4" of concrete + framing = 1.5x65psf). I also use 2 scenario of LL, 40 psf or 3000 psf point load. I use 1 1/8 plywood. I usually design it for 600/L live load or 240/L total load (with the factored DL). My question is, according to IBC, I can only put 4" of concrete. If I have 23' x 23' of garage and the architect wants a drain in the middle, how do I slope the concrete? Is lowering the grade 1" in the middle enough? Can I put more than 4" so I can slope it 1/4"/ft and still have thick enough concrete in the middle? How thick is not thick enough for framed slab? I appreciate your feedback.