Foundation / Slab For Vehicle Lifts

Status
Not open for further replies.

BSVBD

Structural
Jul 23, 2015
463
I have information/data/cut-sheets from (2) competitor suppliers of 2-post vehicle lifts / hoists with capacities of 10 & 12K.

Both suppliers recommend only a 4" concrete slab. When asked about a moment at the base, a rep told me that the anchor bolt layout disperses the moment. How do these slabs NOT fail? What am i missing?

Myself and a colleague both come with 12" of each other in preliminary design in the neighborhood of requiring a 6'x8' footing.

One supplier said, "We've been selling them for years without a problem!"
 
Replies continue below

Recommended for you

I'd check what their assumptions are (in particular their assumed edge distance and subgrade modulus), and see if you agree with them.
 
Not so bad away from the edges. Link. Obviously the anchor bolt spreading business is layperson clap trap.

Capture_m1ulrf.png


I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
We ran into this recently too when repairing an old structure from the 80's. The lifts had been upgraded, so we re-installed them after the slab repairs were complete. Point loads aside, I thought the two post base connection detail was very light.

two-post2_ejhykq.jpg
 