I am working on a project for a rodeo arena. There are existing drilled pier foundation on site. My company is gong to demolish the old bleachers, concrete barrier wall, and concession stands and come in with put new ones. There are existing drilled pier foundations in the soil right now, but we are going to design new drilled piers to support the bleachers that we are adding. The old concrete barrier wall was supported on drilled piers, but I am told that the plan is to come in and support our new barrier wall on a continuous wall spread footing. The new soil report for this project calls for drilled and underreamed footing bearing at a depth of 14 ft below existing grade in the fat clay soils. The footing may be sized for a net allowable bearing pressure of 3000 psf for dead plus sustained live load. The soil report also states that " Allowable bearing capacity at a depth of 24" below existing grade: Dead Load: 1,000 psf and Total Load: 1,500 psf.". I am concerned about using a continuous wall spread footing in lieu of drilled piers when the soil report does not explicitly say to. I have been told to just have the continuous wall spread footing go 3 ft below the finished grade in order to use the 3000 psf allowable bearing. Should I be concerned? Also, we are building concessions stands that will just be rectangles. The walls of the concessions stands will be composed of CMU walls. I have been told to make the foundation a slab-on-grade supported by only grade beams. Based on the soil report information I just provided, is this possible? Any comments are appreciated.