Do you enforce and or provide this service to your customers? See code sections below?
I was teaching a class the other day and was covering this section in the code and I asked the class of 30 ( a mix of fire inspectors and sprinkler contractors) if they did the testing or required the testing. Only 2 in the class indicated they either enforced it or did it. Most did the backflow test as required by many health departments, in NJ it is required quarterly, but few did the forward flow test.
Many had no idea it is required by NFPA 25. What I find interesting is NFPA 13, see below, requires a test header or some way of testing the device. How many plan reviewers or inspectors are enforcing this section of NFPA 13?
The forward flow test is required to make sure the springs are opening at the required flow rate (sprinkler or standpipe system gpm demand) and do not present an obstruction to the flow. The following is what I have witnessed when contractors do this test. A calibrated gauge is installed on the inspection ports on each check assembly. Water is flowed at the system demand and the psi pressure loss is measured between the 2 gauges. The psi pressure loss is compared to the manufactures cut sheet for the backflow device. The psi pressure loss should match the loss at the demand gpm, if it does the device is OK, if not, further investigation is required. The other option is to take the device apart and conduct an internal inspection.
So what do you do?
As per NFPA 25, 02 12.6.2.1* All backflow preventers installed in fire protection system piping shall be tested annually in accordance with the following:
(1) A forward flow test shall be conducted at the system demand, including hose stream demand, where hydrants or inside hose stations are located downstream of the backflow preventer.
(2) A backflow performance test, as required by the authority having jurisdiction, shall be conducted at the completion of the forward flow test.
NFPA 13, 02 Section 8.16.4.6.1 Backflow Prevention Valves. Means shall be provided downstream of all backflow prevention valves for flow tests at system demand.
8.16.4.6.1A: The full flow test of the backflow prevention valve can be performed with a test header or other connection downstream of the valve. A bypass around the check valve in the fire department connector line with a control valve in the normally closed position can be an acceptable arrangement. When flow to a visible drain cannot be accomplished, closed loop flow can be acceptable if a flowmeter or site glass is incorporated into the system to ensure flow. When a backflow prevention device is retroactively installed on a pipe schedule system, the revised hydraulic calculation still follows the pipe schedule method of 11.2.2 with the inclusion of friction loss for the device.
Fire Sprinklers Save Firefighters’ Lives Too
Not ALL Sprinkler Systems Are Created Equal! An Inadequate Sprinkler Design Is JUST As Bad As A Nonsprinklered Building!! When Occupancies Change So Should The Sprinkler System. See NFPA 25, 2002, Edition, Section 4.1.5, 4.1.6 & 4.1.6.1.
So what do you do?