Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Formula for short term horizontal displacement

Status
Not open for further replies.

ak.t

Structural
Joined
Dec 18, 2019
Messages
73
Location
AE
Hi All,
How to calculate the short term horizontal displacement (with adopting cracked section of the concrete) on free standing wall with eccentric footing at bottom, which is subjected to wind pressure alone. This is same as calculating torque of cantilever wall.

Thank you
 
The majority of the deflection will be due to wall rigid rotation as the soil bearing pressures develop.

So, you need to determine a pressure/settlement relationship for your soils.

----
just call me Lo.
 
Considering this as cantilever, i have calculated as follows for short-term deflection (cracked). Here, Mservice is not exceeded the cracking moment.

sep-BW_enxtvn.png


sep-wind_ci2net.png



sep-_cant-_bm_dnmfyr.png


B = 1000 mm
D = 120mm

Ig = 1000 x 1203 / 12 = 144x106 mm4

n = Es/Ec = 200000/ 26587 = 7.52
Fr = 0.62 SQRT (32) = 3.56 N/mm2
Yt = 120/2 = 60 mm

Mcr = Fr*Ig/ yt = 3.56 *144x106 / 60 = 8.544 kNm

Ma = 5.775 kNm

Ma/Mcr <1, Hence Ie = Ig



Deflection = w (uniformly distributed) *l4 / 8*E*Ig

w = 1.1 kN/m = 1.1 n/mm
loaded length = 2500 mm
total length = 3350 mm
E = 26587 n/ mm2
Ig = 144 x 106 mm4

Deflection = 1.1 * 2500*2500* 2500*3350 / 8 * 26587 * 144x 106

= 1.88 mm
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top