Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Force calculation for faults on switchgear bus

Status
Not open for further replies.

buckeyemurphy

Electrical
Nov 28, 2004
9
Is there a standard or typical formula to use to calculate forces on switchgear bus based on available fault current.
 
Replies continue below

Recommended for you

If you mean the Available Short Circuit Current as determined by the transformer impedance, the actual offset current and the resulting forces on the bus bars may be much higher.
You should be calculating the Asymmetric fault current and using that value in your calculations.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 