Footing directly below Slab-on-Grade
jreit
I have a mat foundation which sits ~2'-3' below grade supporting columns.
We have a SOG supporting equipment loads at grade above the mat footing.
What would be the best way to determine the effects (if any) of the SOG loading on the mat foundation?
If you must use a mat foundation, ignore the load from the slab. Alternatively, use square footings under the columns and again, ignore the slab load which contributes nothing to the footing or mat reinforcement.
Is there compacted fill between the SOG and the mat foundation? If so the load just transfers straight down to the mat foundation.
It'll transfer directly to the mat foundation regardless...lack of compacted fill will just mean that the slab settles in the process.
It transfers to the mat foundation, and it transfers through the mat foundation. If anything, it reduces the moment in the mat caused by the columns, but best to ignore that.
If I assume say 12" of compacted fill underneath the SOG and then 2' from there to the top of the mat slab, would using Fadum's chart to calculate the reduced demand on the mat slab be a reasonable approach?
I would assume the DL and LL on the slab acts 2' above the top of the mat slab and use the chart accordingly.
To BA's point, I'll look at the design both with and without the SOG loading.
If the soil is essentially confined, then no, I would not reduce it. It may not influence the moment in the mat appreciably, but it will influence the pressure beneath the mat.
My elevation view wasn't clear so I've attached a plan view also.
The pressure should be able to spread out and dissipate around the sides beneath the SOG.
Would you still consider that a confined condition resulting in 100% load transfer from the SOG to the mat?
This is different than I pictured. Why are you using a mat at all? Can you use a footing for each column and a separate slab?
Is your concern trying to optimize the mat, and thus you are trying to account for reduction of the magnitude in area loading from the slab as it spreads through the soil?
If so, I agree with others here, used spread footings under the columns.
Yes, exactly TRAK.Structural, I am trying to optimize the mat foundation design and use a reduced loading if possible.
The column spread footing is also a reasonable approach but the final call on that is made by other disciplines.
If we do go with the mat, would the Fadum chart approach to determine a reduced loading be reasonable?
jreit - I'm not familiar with that chart, but the concept looks reasonable. As some others have stated though, I doubt the reduction in vertical stress from the spreading of the slab on grade load will have much effect on the structural design of the mat. This load should transfer straight through to the bearing soil below.
Personally I would consider it largely safe to ignore the loading for the mat foundation design and only consider it relevant from a soil bearing pressure aspect. Whether you ignore any spreading out of the load or not, in my mind I would just assume the mat takes the load straight down rather than redistributing and reduce the soil's bearing capacity by the same amount, for simplicity.
Why yes, I do in fact have no idea what I'm talking about
I want to make sure I'm understanding this correctly. The SOG really just transfers the 400 psf load directly down to the soil. That 400 psf is not resisted by the mat foundation directly. I should analyze the mat for the column loading and add 400 psf to the resultant soil pressure underneath the mat for the bearing pressure check.
I'm not sure how that 400 psf is getting underneath the mat? Why is it ok to not design the mat foundation for that 400 psf load?
Because the 400 psf load plus the weight of the mat are transferred directly to the subgrade. If you didn't have a mat, the grade slab would bear directly on the soil. The columns are putting tension on top of the mat, hence its weight and the 400 psf soil load are reducing the stress in the mat.
There is no reason mentioned so far, to use a mat. You should be using a footing under each column and omit the mat.
Flip the system upside down:
The "heavy" slab on grade load gives a similar effect to post-tension balanced loading
Ultimately the "benefit" of the SOG loading depends on the relative magnitude between that loading and the column reactions.
Turning it upside down is a good way to understand the statics of the situation, but remember that, even if the "SOG Load" is more than required to benefit bending in the mat, mat deflection is limited by the presence of the subsoil. If you insist on having a mat, its behavior should be treated as a mat on an elastic foundation. Unless there exists some convincing reason for using it, the mat should be omitted in favor of four separate footings.