Assuming that the soft starter is set to initially reduce the voltage to 75%, then starting current will be reduced 75% as well and torque will be 56.25%.
Essentially, yes. But keep in mind that the limited values are of the motor's basic torque speed curve, not of FL values. So for instance if you limit the voltage to 75%, the initial starting current will be reduced to 75% of the DOL current, which is already 600% of FLC, therefore your initial current will be 450% (75% of 600%) and your torque will be 56.25% of 160% FLT, or 90% of FLT.
Is my understanding correct if I say that the current limiter feature of the SS will be set to stop the starting process once the pre-set motor acceleration time is exceeded so as not to exceed the motor thermal limits.
First off, realize that Current Ramp and Current Limit are two different things. Speaking then of Current Limit, no, you are misunderstanding that. The Current Limit function of a soft starter will not, in and of itself, monitor what is happening in the motor. It just limits the current to a maximum setting. If that produces insufficient torque to continue accelerating the motor, eventually the Thermal Overload function will be expected to take the starter off-line. Some soft starters also have a maximum Acceleration Time Limit feature which will not wait for the OL function in case the motor does not fully accelerate, but this feature is not universally available unfortunately.
What is the difference between voltage ramp and current ramp associated with SS starting?
I don't have much to add to LionelHutz's response, other than as a gross generality, Current Ramping tends to be a little smoother on some applications, for whatever that's worth. In 99.99% of applications, you will not notice much of a difference.
I do a lot of commissioning for a brand of soft starter that has all available ramp profile methods available in it, so I have tried them all on a few applications. I can barely tell the difference and generally default to Voltage Ramp with a Current Limit.