Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Foam sprinkler system

Status
Not open for further replies.

TravisMack

Mechanical
Sep 15, 2003
1,766
Are you required to maintain a uniform discharge in a closed head vs. open head foam system. With a foam deluge system, you are required to size the piping so that any sprinkler does not discharge more than 20% of its required discharge. Is this true of a closed head system as well? I do not do many of these systems, so I just want to check myself.
 
Replies continue below

Recommended for you

Travis:

What standard are you citing? NFPA 13 is silent on this (using the 2002 edition).
 
The closed foam system is the same as a wet system as far as hydraulics are concerned, see NFPA 16. All u need to know is the design density, design area, % of foam concentrate, and duration.

Example, If u look at NFPA 30 2003, table 6.8.2 (d) for 1B liquid <5 gallons, for palletized storage, u need .30/3000, if u use a 3% foam concentrate, .30 x 3000= 900 gpm x .03= 27 gpm for foam concentrate times say 20 minutes of foam duration is 540 gallons of foam. Add 100 gpm for inside hose station, another 3 gpm of foam, or another 60 gallons, so u need 600 gallons of foam concentrate.

I like Viking product Low Flow Foam System, can discharge over a wide range of flows.

Tom
 
Reference NFPA 16. I was having a brain fry for the thing and wanted some one else to agree that we didn't need to do the same as for the deluge.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor