Ok, sorry I was trying to simplify the problem.
My problem does not relate directly with nfpa 11, but I have to following FM 7.88. I attached the chapter, highlighting in yellow the part that gives me some problem. Worth mentioning that the liquid has a flashpoint below 93° . In order to have more informations about foam hose stream and foam monitor nozzle I used the definition in NFPA 11 that in clause 3.3.26.1 defines the Foam Hose Stream, A foam stream from a handline and in clause 3.3.20.1 defines Fixed Monitor as A device that delivers a large foam stream and is mounted on a stationary support that either is elevated or is at grade.
Watching this chapters it is very difficult to understand how many foam monitors nozzle should be considered to work simultaneously and that could be a problem, since looking at some datasheet the working flow rate are more than 1500 lpm for each foam monitor nozzle.
An other thing that is not clear for me it is how usually the foam monitor are actuated, I now that each foam monitor can be actuated manually, but I don't know how the foam system can be sctuated.
I hope that this can explain...