Can anyone tell me that Why and for which Process condition Flushing connections required(For Diaphragm Seal Transmitters)??
 
Sludge or precipitating deposits that can block pressure transfer to the diaphragm need to be removed by flushing.

For instance, Lime slurry will deposit both lime and impurities that over time will block the slurry's hydrostatic pressure from contacting the sensing diaphragm.
 