Ok all:
we have been working on a system with 10 ppm of Fl 100 ppb of AS PH raw at 8 - 8.5 and average temp of 112 F and a flow rate of 10GPM:
we are using Actavated Alumina.
my personal opion as that although it is working it is labor hevaythe steps are in this order:
1. ad acid to lower the PH to 6.0 (5.5-6.5)
2. run water through the AA bed alowing for a contact time
of about 5 min / per gal / per cubic ft of medea
3. check PH on outlet for minimum of 7.0 and monitor FL at
this point.
we have found that our plant does not work the same as the plant 5 miles down the road. so you will need an operator that can spent the time "tweeking" the system we have found that our plant optimises when the outlet PH is at 8.0 .. also, you will have a fair amount of backwash water to deel with we are using evap ponds here.
you might also look at using RO the initial cost looks more but the time and additional outlay for A.A. add up fast!!! (chem injector pumps, safty shower, chemicals, operator time, *there is not any training I have found so it is all OJT to lern how to make it work* and the list goes on and on).
by the time we figured out that RO would have been more cost effective we were committed to the A.A. system. (over 40K commited for a customer base of 18, RO would have cost us about 25K - 30K for the flow rate we need and allowed for the first year of O&M.)
good luck and let us know what you do and how it works out for you.
h2oman