Dec 3, 2019 #1 vreijb Electrical Joined Nov 22, 2006 Messages 38 Location CA I would like to know if I need to change the fluke 435 default current Range 3000A to be close to load current or keep as is to start measurement as the manual suggest. The panel I will connect has total load of 100A.
I would like to know if I need to change the fluke 435 default current Range 3000A to be close to load current or keep as is to start measurement as the manual suggest. The panel I will connect has total load of 100A.
Dec 3, 2019 #2 mparenteau Electrical Joined Mar 12, 2019 Messages 146 Location US Keeping it in the default setting will be fine. Mike Upvote 0 Downvote
Dec 5, 2019 Thread starter #3 vreijb Electrical Joined Nov 22, 2006 Messages 38 Location CA Thanks. If you measure a panel with 3 phase 3 wire, which connection to be made? Delta or Y IT on the fluke. I guess both should work. Upvote 0 Downvote
Thanks. If you measure a panel with 3 phase 3 wire, which connection to be made? Delta or Y IT on the fluke. I guess both should work.
Dec 5, 2019 #4 mparenteau Electrical Joined Mar 12, 2019 Messages 146 Location US Connections are straightforward per the manual. Mike Upvote 0 Downvote
Dec 5, 2019 Thread starter #5 vreijb Electrical Joined Nov 22, 2006 Messages 38 Location CA Not really in this case. I got Fluke Technical support recommendation to use Delta. I got feedback from experienced technician to use Y-IT. Upvote 0 Downvote
Not really in this case. I got Fluke Technical support recommendation to use Delta. I got feedback from experienced technician to use Y-IT.