TravisMack, There is no reduction possible in fire flow as almost all buildings except one are non sprinklered. Yes I have selected the pump with fire flow gpm and Sprinkler demand pressure. But one of the manufactures told me that 5 bar pressure is too low for hydrants, It has to be minimum 8 Bar. Thats the reason I am confused now.
Stokeyfpe, I am sizing the pump for both Fire flow & Sprinkler demand. 300 gpm is only sprinkler demand where as fire flow demand is 3250 gpm from IFC Appendix B.