Short answer, no. Note that 8.6.5.2.2 ends at 18" below the deflector. Not coincidentally, this is where the obstruction rules for standard spray heads change. NFPA 13 2010 is giving a spacing credit for light hazard occupancies that doesn't extend to ordinary and extra hazard. Therefore, if the obstruction was 18" or closer to the deflector, you would treat it as a wall and space accordingly. If it was greater than 18" below the deflector, you would apply NFPA 13-2010 8.5.5.3. If your floor mounted obstruction doesn't fall into one of the "sprinkler required below" categories, then go on your merry way and space heads as if it didn't exist.