I have a question about Code R502.7 in the 2009 IRC. It states that “Joist shall be supported laterally at the “Ends” by full-depth solid blocking and so on. The Exception says that “In Seismic Design Categories ……..restraint shall also be provided at each intermediate support.
I take this to mean that blocking is required at Both Ends of the joists, and “Intermediate Support” to be defined as a support somewhere within the span of the joists.
If I am correct then I would assume that in Any Situation involving two single span joists, laterally supported at the exterior walls with a rim joist, and meeting on top of a support beam at the interior of the house, they would also require lateral resistance blocking over that support.
Again if the above is correct: If the blocking is laterally supporting the end of two joists over the support beam, does this mean that it is acceptable to only block every other joist bay assuming that the floor sheathing on top of the joists will transfer the lateral load to the next block?
I take this to mean that blocking is required at Both Ends of the joists, and “Intermediate Support” to be defined as a support somewhere within the span of the joists.
If I am correct then I would assume that in Any Situation involving two single span joists, laterally supported at the exterior walls with a rim joist, and meeting on top of a support beam at the interior of the house, they would also require lateral resistance blocking over that support.
Again if the above is correct: If the blocking is laterally supporting the end of two joists over the support beam, does this mean that it is acceptable to only block every other joist bay assuming that the floor sheathing on top of the joists will transfer the lateral load to the next block?