resqcapt19
Electrical
- Aug 29, 2001
- 535
I recently worked on clearing a ground fault on a 1200 amp 3 phase 480 volt service. After the ground fault was cleared I had 490 volts phase to phase and about 900 volts phase to ground on all three phases. It was discovered that when the utility built the transformer bank they did not connect the primary wye point to ground as required by their standards. I understand that with both sides of the transformer bank floated that the voltage to ground can be just about any value and I understand that there is very little current to ground, but my question is, can this voltage to ground damage the conductor insulation over time?
The utility did connect the primary wye point to ground and the voltage to ground on the secondary went down to ~300 volts to ground.
Don
The utility did connect the primary wye point to ground and the voltage to ground on the secondary went down to ~300 volts to ground.
Don