I've unsuccessfully searched the internet several hours for a supplier of a heavy-duty, 42" diameter, spiral-wire-reinforced, flexible duct for conveying clean ambient air at 5" WC. Does anyone know where I might find such an animal?
 
Replies continue below

Recommended for you

That does sound rather large. Probably 20" is the max normally available. I've spec'd/seen some 42" diam. fabric ducts like DuctSox, but that's probably not what you had in mind.

Could you not employ some smaller parallel paths to accomplish this task?

 
No, it's an existing duct arrangement used in four different places so it would be a big deal to modify them all - even if I could get the funding approved. The existing 42" flex ducts are almost 30 years old and I can't find any record of who the original suppier was. I found that sells flex duct up to 60" diameter, but their's can't take the 5" WC pressure.
 
Thanks Chris, ABC says they can make it - I'm waiting for a quote now!

Nice study EmeraldCoastHVACR, that one goes in my references folder.
 
Contractors and I always have discussions about length of flex duct and the manner in which it is installed. I detail its use carefully both on drawings and specifications and contractors pooh-pooh the reasons for the details but do it after they have to remove and replace a couple of pieces.

I have seen the bad results of sloppy flex installations in too many balance reports.

I knew about the high pressure loss, but the paper indicates that my calculations are off by about 10%. All the more reason to limit the use of flex duct.

Excellent paper.
 
I'm glad they could help, they're a good bunch down there. I worked on the expansion to their plant a few years back.
 
To summarize that paper:

The only time flex came close to galv steel was fully extended and there was considerable loses when at 94% efficiency, which is extremely rare (i've never seen it) in the field.

Expect to see flex duct losses approaching 50% compared to galv metal; in addition, expect to see losses using ductboard with liners more than 33% compared to metal(ASHRAE design manual).

From a techs point of view, my experience shows that ductboard & flex systems lower seer ratings 2 to 3 points with all the deteriorating effect that low-airflow systems give(too numerous to mention here).
 