I am analyzing a control valve on the liquid effluent from a two phase (liquid/vapor) flash drum. The liquid is a physical solvent (Selexol) and contains approx. 8% (wt.) CO2. The pressure at the valve’s inlet flange is 185 psig, which is basically the flash drum’s pressure. The pressure at the outlet of the valve is 15 psig. The liquid in the upstream drum is stored at its bubble point due to the dissolved CO2, but the solvent itself has a very low vapor pressure (<1 psia). The true critical pressure of the gas rich solvent is not known, but is the pseudocritical pressure is approx. 1350 psia.
Operating data from the plant indicates that the control valve is only running at 30% open. My calcs using Fisher’s liquid sizing equation of dP allowable = Km*(P1-rc*Pv) indicate the valve is choked (dP allowable of 24 psi vs. dP actual of 170 psi). Using the dP allowable as the pressure drop in the valve sizing equation shows that the valve should be running at 70% open. All indications are the trim in the valve has not been replaced since the valve was shipped from the factory.
Finally, the Question: Is there something special about sizing control valves for this application (physical solvent with a large amount of absorbed gases) that would make equation of dP allowable invalid? If so, please explain. The only other thing that I can think of is that the sever flashing service has caused plug erosion and changed the valve trim characteristic from linear to something resembling quick opening.
Would appreciate any feedback on this.
Operating data from the plant indicates that the control valve is only running at 30% open. My calcs using Fisher’s liquid sizing equation of dP allowable = Km*(P1-rc*Pv) indicate the valve is choked (dP allowable of 24 psi vs. dP actual of 170 psi). Using the dP allowable as the pressure drop in the valve sizing equation shows that the valve should be running at 70% open. All indications are the trim in the valve has not been replaced since the valve was shipped from the factory.
Finally, the Question: Is there something special about sizing control valves for this application (physical solvent with a large amount of absorbed gases) that would make equation of dP allowable invalid? If so, please explain. The only other thing that I can think of is that the sever flashing service has caused plug erosion and changed the valve trim characteristic from linear to something resembling quick opening.