Squirrel - OK, so this is an existing installation. That wasn't clear from the original post. From a mechanical strength perspective, there's probably very little risk. But, one can't talk about a pipe's temperature limits independently from pressure. The allowable stress is a function of both.
So, the existing pipe is nominally limited to 110C at XX psig. What is that pressure value? 110C is a very low temperature limit for piping, so I'm guessing that the value of XX is way higher than the actual pressure you'll see in the flare header during this scenario. In other words, it's very unlikely that this pipe will be close to it's internal stress limit when the temperature is 140C.
The more important question is what impact does this have on the pipe design (expansion/contraction)? This is something that's often overlooked, and it's a real risk for flare headers. I'm familiar with a number of flare hdrs which have experienced loss-of-containment failures because of thermal stresses. Plant personnel generally regard the flare header as a garbage can, and they think they can toss anything in without any reason to be concerned. That's not true. One must be cautious about the following combination of events:
- dumping a high flowrate
- at an unusually high or low temperature
- over a long period of time
If those three points apply to the case which we're discussing, then have a pipe stress analysis performed before proceeding. Otherwise, there's probably no problem.