What type of flare is it? A conventional open pipe type flare is good to 50% mach at the outlet tip. Velocities down the flare header should not exceed 50% to 70% mach (70% mach more typically applies to laterals, not the main flare header). I'm not sure I know what you mean by 'I know how much NG I can feed and the waste gas composition'.
Then there is the question of radiation on surrounding equipment, property lines, operating areas that needs to be checked out.
Capcity of the flare drum should also be checked, that method is summarized in API 520/521.
If it's a sonic type type, I suggest getting the vendor involved.