is there any problem if I fit the nozzle flame arrestor on center roof tank?, then what is the better location
 
Which way is the flame front travelling? Towards the tank from a pipe, or from inside the tank out a pipe?

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
I would recommend talking to these guys.


Note: I am not a representative, and do not have an interest in Enardo.

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
Note that API-2000 has a statement saying you don't need a flame arrestor if you have a P/V vent.
 
Flame arrestors can ice up and prevent the P/V vent from working properly, leading to tank collapse inwards when you withdraw liquid.
 